triptolemus wrote:
We reduced the PPE on this arc flash study... hard to make out, but the label indicates HRC 3 inside 120/208 panel. When I reviewed the study data, it took me no time at all to notice they entered breaker clearing times of 2 SECONDS rather than 2 CYCLES into their spreadsheets... Needless to say, I reduced the PPE requirements.
Are you sure the 2 seconds has not been chosen because of a low arcing current?
IEEE1584 has a 2 seconds rule to limit the incident energy based on the thought that a worker will get out the way after an arc ignites (if he has a place to go).