It is currently Sat Oct 03, 2026 10:04 pm
 Post subject: Anyone seen a new OSHA requirement that for transformer denergization
PostPosted: Fri Jan 07, 2011 10:23 am
Recently a customer had heard that OSHA was requiring transformers to be de-energized prior to operating breakers on the secondary. They asked me about that and I had to tell them I would make some inquires and get back to them.
That is something that I have not seen or come across yet and was wondering if anyone had seen it or heard of it as an upcoming possibility?
PostPosted: Fri Jan 07, 2011 1:32 pm
OSHA takes decades to update their standards, so this is more then likely a NEC requirement for 2011, maybe in Article 450 somewhere.....
PostPosted: Sat Jan 08, 2011 8:56 am
Have not heard of it and it makes no sense anyways. What is the reasoning here?
In a typical MV/LV substation most often the MV switch on the pirmary side of the transformer has a much lower arc flash hazard than the LV main breaker on the secondary side. Which has led some companies to have a procedure to open the MV switch before operating the LV main.
Maybe this is where your "somebody" became confused. :confused:
Problem with this thinking is often the MV switch is not designed for this duty. In fact there are usually interlocks thee to prevent this sequence. I have actually seen plants override key interlocks to do this because they think it is safer. :eek:
Even if the MV switch is a load break switch and by design can be operated under load they do not like to do it too often, so if this is a common task, those switches will fail. In fact I have a crew out repairing switches like this because of this "procedure" this weekend.
