It is currently Fri Aug 21, 2026 11:01 am
 Post subject: Maximum Fault Durations
PostPosted: Wed Aug 04, 2010 8:00 am
I can understand the reasoning IEEE 1584 is using for the 2 second rule of arc duration for personal arc flash protection, but is this not ignoring other issues such as equipment damage and even possible fire hazards for the entire switchgear, transformer, or building. Also considering down time for equipment replacement versus a possible quick clean-up and re-energizing. Just wondering what everyones view is on this and what the latest industry norms are for the max duration. I don't care for the 2 second rule for the reasons above but at the same time think a 1/2 mile arc boundary is ridiculous.
PostPosted: Wed Aug 04, 2010 9:00 am
The 2 second rule is more of a temporary fix IMHO. When IEEE 1584 was released in 2002, it was an amazing effort but it could not cover everything.
One of the open issues was low fault currents leading to long clearing times that can produce some "unique" arc flash protection boundaries. A 2 second cut off was added as "something is better than nothing" for a cut off that can be used with good judgement when excessive clearing times are an issue. This is based on human reaction time.
New research is slowly coming and it will perhaps provide a more realistic way to look at this. For now, 2 seconds is as good as gets if you want something that can be tracked back to a standard. At 208V and low short circuit current, the arc often can not even sustain.
PostPosted: Wed Aug 04, 2010 11:32 am
The two second rule also implied that the person subjected to the arc flash/blast will be able to get away or be thrown away from the immediate area. If the enclosure or area surrounding the work is small or confining or the worker is in an awkward position, then sound engineering judgement must be used in order to justify the use of the two second rule.
PostPosted: Wed Aug 04, 2010 11:40 am
Absolutely! That is why I mentioned judgement in my second paragraph. Not having space to get blown clear or jump back would present a major issue with the 2 second rule. Also, I have been studying this a bit with a few others and the typical first reaction is not so much to jump back but to put your arms up and turn sideways. Then you jumping back. Picture someone throwing a bad pitch at you.
- Thanks for your comments.
PostPosted: Thu Aug 05, 2010 6:15 am
A problem with most (all?) formulas, is they assume the arc will maintain constant characteristics throughout the entire clearing time. There is no accommodation made for the increased arcing resistance that will occur as the arc is lengthened due to material being 'consumed', likewise the effect of plasma is not considered.
PostPosted: Fri Aug 06, 2010 7:37 am
Arc hazard analyis is for personnel safety only and is not intended to provide any protection for equipment.
PostPosted: Fri Aug 06, 2010 8:24 am
Agreed. And the 2 second rule is an assumed exposure time for someone exposed to a longer duration arc who begins to move away. It has nothing to do with the actual arcing time the equipment might be exposed to.
If you are concerned with equipment damage at the arc location, suggest you look into arc resistant switchgear. 1584 is out of scope.
If you are concerned with fire protection, 1584 is again out of scope. Try some of the NFPA standards or building codes.
PostPosted: Wed May 04, 2011 11:17 am
Regarding Jim's previous comment :
"New research is slowly coming and it will perhaps provide a more realistic way to look at this. For now, 2 seconds is as good as gets if you want something that can be tracked back to a standard. At 208V and low short circuit current, the arc often can not even sustain."
I understand then that, pending further arc duration research, where the arcing current is low enough to result in prolonged OCPD clearance times, the actual arc duration is difficult to impossible to predict. Therefore we should assume the arc may sustain until cleared by the OCPDs, even when it seems that probably would unlikely be the case. Which will give us high, but conservative Ei results.
But then, as Jim pointed out, at some lower voltage and current levels it is known that an arc cannot sustain. By this, I take it that the arc will always extinquish almost immediately - say, no longer than 1 cycle.
Have any certain voltage, amperage, and/or gap parameter thresholds been established for which one is justified in assuming an arc duration of less than 1 cycle ?
For example, a case at 480V, but where the arc current is quite small, or the gap quite wide ?
PostPosted: Thu May 05, 2011 9:21 am
There are a few recent papers out there discussing fault durations, at LV levels, based on actual testing conducted by EPRI and other Utilities.