Dear collegues, I'd like to ask for your opinion about Article 90.2 Scope of NFPA 70E 2009:
"(B) Not Covered. This standard does not cover the following:
(5) Installations under the exclusive control of an electric utility where such installations:
c. Are on property owned or leased by the electric utility for the purpose of communications, metering, generation, control, transformation, transmission or distribution of electric energy."
My questions is: Why Electric Utility must not accomplish with NFPA 70E but industrial plant are covered with that standard?
Does it mean that Utility' s workers are not exposed to arc flash accidents?
Take NFPA 70E into account switchgears with internal arc classification (IEC 62271-200)?
Thanks for quickly answer.
PAD
PostPosted: Mon May 03, 2010 8:25 am
The National Electrical Safety Code (NESC) published by the IEEE covers electric and communication utilities.
PostPosted: Mon May 03, 2010 9:06 am
Utilities are covered by other safety standards in the US (ANSI C2 - National Electrical Safety Code).
Their workers are definitely exposed to arc flash hazards. At the same time, a utility must put greated emphasis on maintaining their service to their clients than a typical industrial plant. Also, some classes of utility workers are almost never exposed to three phases arcs because of the distance between phase conductors.
PostPosted: Mon May 03, 2010 1:17 pm
You mean distance between conductors in utility swichtgears are different from industrial switchgears?
I think both use same switchgear, and probably incident energy could be similar, so risk is the same in utility and industrial panels.
PostPosted: Mon May 03, 2010 1:22 pm
Using the same gear, the risk is the same.
But on more typical utility equipment, the risk is different. More typical as in distribution or transformation buildings/yards.
Note that utility workers, in buildings used other than "for the purpose of communications, metering, generation, control, transformation, transmission or distribution of electric energy", fall under 70E.
PostPosted: Mon May 03, 2010 1:48 pm
But no covered by 70E means that workers don't need use arc flash PPE?
PostPosted: Mon May 03, 2010 1:51 pm
The NESC, not 70E, spells out the PPE for utilities. They still use PPE.
PostPosted: Mon May 03, 2010 1:52 pm
NO!
It means the standard which covers these workers (and how to protect them, including choosing the proper arc flash PPE) is, as previously said, in ANSI C2, also referred to as the NESC.
PostPosted: Mon May 03, 2010 4:59 pm
[url="http://www.arcflashforum.com/forumdisplay.php?f=13"]http://www.arcflashforum.com/forumdisplay.php?f=13[/url]
PostPosted: Wed May 05, 2010 10:49 am
Vincent B. wrote:
NO!
Ok, I haven't red NESC yet. Then I ask if NESC talk about arc flash hazard study acording to NFPA 70E or IEEE 1584.
I think arc flash PPE by 70E and NESC is the same
PostPosted: Wed May 05, 2010 1:16 pm
About the only thing common between the two is electricity and a calc for PPE. Most use ArcPro software for OH utility distribution.