 Post subject: Incident Energy Calculations-1
PostPosted: Sun Jun 22, 2025 8:36 am
Dear Engineers.
Greeting.
I want to do the Incident Energy calculations for 33 KV GIS switchgear & 66KV / 120 KV / 220 KV Load Break switch in the Outdoor switchyard ( Transmission line Power entering in the outdoor open air switchyard ).
What is the best method to calculate ? Because I know that IEEE-1584 2018 can not be used.
Please advise.
Thanks.
Mubin / Africa.
 Post subject: Re: Incident Energy Calculations-1
PostPosted: Mon Jun 23, 2025 9:54 am
viewtopic.php?f=4&t=2370
Read this and then repost your question(s) if you have any.
Mike
PostPosted: Wed Mar 11, 2026 12:20 am
MUBINULLAH KOTWAL wrote:
Dear Engineers.
Greeting.
Please advise.
Thanks, Space Waves.
Mubin / Africa.
For HV equipment like 33 kV GIS and 66–220 kV outdoor switchyards, IEEE 1584-2018 typically isn’t applicable. Many engineers instead reference IEEE 1584 Annex D, EPRI, or CIGRÉ guidance for transmission systems, considering arc current, protection clearing time, and working distance.
PostPosted: Wed Apr 01, 2026 8:28 pm
I'm seeking advice on Incident Energy calculations for high voltage switchgear. Specifically, I'm dealing with 33 KV GIS switchgear and 66KV/120KV/220KV Load Break switches in an outdoor setting. I know IEEE-1584-2018 isn't applicable here, so what is the recommended approach? This feels like navigating Granny's house – you know something's there, but finding the best path is tricky! Any input would be greatly appreciated.
PostPosted: Fri Jun 12, 2026 6:49 pm
I recall a Level Devil situation at a manufacturing plant where we were retrofitting an old panel. The original drawings were...aspirational. We had to perform on-site energy calculations due to outdated and incomplete documentation, delaying the project and highlighting the very real risks of untested assumptions.