Post subject: regarding to "e" and "E" used in Table 2 of Coefficient Posted: Sun Aug 27, 2023 3:06 am |
Hello everyone. I am starting to do self-study the IEEE 1584:2018 standard for arc-flash calculation. During the reading of the data from Table 2 Coefficient for Equation (2), I found there is different written of wording.
For. e.g, for K2 factor: "−6.0287E-05" for VCBB is described and "−3.097e-06" for HCB is used.
My question is for "e" in the table data sheet is it just mistake which shall be to "E" instead? for e.g, "−3.097e-06" corrected to "−3.097E-06" = "-3.097x10-6".or, there is different meaning for "e", for e.g, "natural logarithm"? Thanks for your help.
| Attachments: |
| Top |
Jim Phillips (brainfiller)
Post subject: Re: regarding to "e" and "E" used in Table 2 of Coefficient Posted: Sun Aug 27, 2023 5:07 pm |
| Plasma Level |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1738 Location: Scottsdale, Arizona
I believe that is a typo since these are all coefficients in scientific notation. It has been added to the list for next time.