It is currently Wed Aug 12, 2026 8:11 am
 Post subject: Short Circuit Study - Motor Contribution
PostPosted: Tue May 10, 2022 3:05 am
When developing a model in order to run short circuit analyses, is it recommended to group LV motors <50HP? Upon looking at IEEE 399 and IEEE 551, this appears to be typical. Are individuals utilizing this technique or modeling all LV motors individually?
Thanks for the input.
 Post subject: Re: Short Circuit Study - Motor Contribution
PostPosted: Tue Jul 12, 2022 1:03 pm
Hello, I'm in the UK where we typically run short circuit studies in accordance with IEC 60909. That standard suggests that "for simplification of the calculation" groups of asynchronous low-voltage motors "may be combined to a single equivalent motor". We generally follow this advice with our modelling and combine LV motors at each switchboard or MCC.
However, if there is a particularly large LV motor that may dominate a scenario (for example, an electric driven fire pump that is online when the system is in emergency mode) then we do model that as a standalone motor so we can switch it in/out as necessary.
Combining LV motors also reduces the task of data collection! We typically only ask for detailed motor data for the largest LV motors - this is in case we need to add them for a particular scenario, or for use in other studies such as coordination.
Nick Bramhall, CEng
safearc.co.uk