It is currently Fri Nov 06, 2026 11:47 pm
What are your/company preferences for arc flash labels?
Nominal Voltage 17%  17%  [ 36 ]
Arc Flash Boundary 15%  15%  [ 32 ]
Incident Energy and Working distance 17%  17%  [ 36 ]
Arc Flash PPE Category 5%  5%  [ 10 ]
Minimum arc rating of clothing 8%  8%  [ 16 ]
Site specific PPE level 6%  6%  [ 12 ]
Limited and Restricted approach boundary 11%  11%  [ 24 ]
Date 15%  15%  [ 31 ]
List of PPE requirements 6%  6%  [ 12 ]
Something else - please tell us! 1%  1%  [ 3 ]
Total votes : 212
 Post subject: Arc Flash Label Data - Revisted
PostPosted: Sun Oct 24, 2021 12:57 pm
Arc flash (equipment) labels and data have been discussed in the past but practices evolve over time.
The 2021 Edition of NFPA 70E has minimum requirements for labels which includes:
(1) Nominal System Voltage 130.1(H)(1)
(2) Arc Flash Boundary 130.1(H)(2)
(3) At least one of the following:
a. Available incident energy and the corresponding working distance OR the arc flash PPE category
b. Minimum arc rating of clothing
c. Site-specific level of PPE
Here are a couple of references regarding labeling:
Article: Arc Flash Labels Simplified
Arc Flash Labeling Requirements and Strategies Free On Demand Video Class
To gauge the evolution of labeling, this week’s question is a follow up to a similar question asked quite some time ago.
• Nominal Voltage
• Arc Flash Boundary
• Incident Energy and Working distance
• Arc Flash PPE Category
• Minimum arc rating of clothing
• Site specific PPE level
• Limited and Restricted approach boundary
• Date
• List of PPE requirements
• Something else - please tell us!
 Post subject: Re: Arc Flash Label Data - Revisted
PostPosted: Mon Oct 25, 2021 10:33 am
We also include the following items:
1. Our company name.
2. Our company phone number.
3. Our Job #. (this is helpful for when we do a AF refresh study after 5 years.)
4. Maximum available fault current.
5. Standard Version used to calculate the AF energy and boundaries.
PostPosted: Mon Oct 25, 2021 1:04 pm
I would add that Robert's example above also contains an ANSI signal word and symbol.
PostPosted: Tue Oct 26, 2021 7:54 am
Having the maximum available fault current is a huge plus. I think by adding that number people will gain a much better appreciation of what arc flash energy is all about. Strangely, too many people order gear without even knowing what the available fault current even is.