It is currently Wed Oct 28, 2026 8:29 pm
Do you consider operating a CB for the 1st time after installation/maintenance a low arc flash risk?
Yes 19%  19%  [ 6 ]
No 69%  69%  [ 22 ]
Not sure 13%  13%  [ 4 ]
Total votes : 32
 Post subject: Operating CB for first time after installation / maintenance
PostPosted: Sun May 31, 2020 3:54 pm
Do you consider operation of a circuit breaker or switch the first time after installation or completion of maintenance in the equipment as a low arc flash risk - i.e. low likelihood of occurrence? Assume the 6 conditions of “normal� have been met – Properly installed, properly maintained, etc.
Do you consider operating a CB for the first time after installation or maintenance a low arc flash risk?
Yes
No
Not sure
 Post subject: Re: Operating CB for first time after installation / mainten
PostPosted: Mon Jun 01, 2020 4:04 am
I voted Not Sure as this is a wide class -CB. Are we referring to MCCB, ICCB or LVPCB? What about vintage breakers like from the 1960' that have just been PM'd and this is the first operation of it back in the cubicle? What about a breaker in a MCC bucket where the bucket was removed, PM'd and re-installed? Are stabs lined up properly?
I think each case has to be examined from a risk perspective on the first operation.
