It is currently Sat Aug 08, 2026 5:05 am
 Post subject: Things you find on data collection
PostPosted: Tue Mar 21, 2017 10:20 am
Just never know what you will find when you open a panel. :o Apparently this is a method to isolate the conductors from touching the panel
 Post subject: Re: Things you find on data collection
PostPosted: Tue Mar 21, 2017 11:59 am
It seems to have worked didn't it? Is that in the NECA manual?
95% Retired
PostPosted: Sat Mar 25, 2017 11:01 am
I wonder what the creepage and flashover ratings are for cardboard.
PostPosted: Mon Mar 27, 2017 6:56 am
I believe that is called cardboard-clad switchgear!
PostPosted: Mon Mar 27, 2017 12:26 pm
This is what we typically find when we do data collection at sites.
Outdated (or non-existent) One line Drawings
Underrated (SC) Equipment
Oversized / Undersized Equipment
Poorly Protected Equipment
Poor Coordination of Protective Devices
NEC Code Violations
Broken or Unsafe Equipment
Cracked cases
Broken covers, hinges, latches, or handles
Dead animals
These Studies with data collection are like an Equipment Safety Audit.