It is currently Thu Oct 22, 2026 2:41 am
 Post subject: Arc Blast Hazard
PostPosted: Fri Apr 08, 2016 11:23 am
Here is a theoretical review of what is plausible regarding arc blast until more data is published. The summary is that there is a lot of fear mongering out there that doesn't hold up.
arc blast hazard revisited.pdf [297.88 KiB]
Downloaded 2529 times
 Post subject: Re: Arc Blast Hazard
PostPosted: Wed Nov 29, 2017 9:26 am
Our paper of 2 years ago assessed the models.
http://ieeexplore.ieee.org/document/7499702/ and did some real measurements with sensors that didn't peak and with a physical method.
Our new paper goes further and can be attended at the IEEE Electrical Safety Workshop in 2018
http://www.ewh.ieee.org/cmte/ias-esw/registration/register.php