It is currently Mon Sep 28, 2026 11:46 pm
 Post subject: is arc flash catagory reduced?
PostPosted: Mon Dec 08, 2008 11:39 am
When a mcc bucket is locked out does this affect the flash catagory rating? example a bucket rated a cat 3 is locked out do you still need cat 3 ppe to open the bucket to view the unit?
PostPosted: Mon Dec 08, 2008 1:16 pm
No it is not, the hazard exists from what is upstream of the MCC so locking it out changes nothing in that cell.
PostPosted: Mon Dec 08, 2008 7:04 pm
Arc Flash is about working on or near live parts. The only problem with a locked Mcc bucket is that it is only deenergized on the load side of the breaker or fuse switch - the line side is still energized. If the designed incorporated some type of shield or guard that prevented touching live parts then I think you could make a case for it being outside of AF requirements.
