It is currently Sat Aug 22, 2026 7:20 pm
 Post subject: 4 Foot Flash Protection Boundary??
PostPosted: Wed Jul 04, 2007 8:02 am
We are in the middle of conducting our first arc flash study. We are getting many calculated flash boundaries of less than the 4 foot distance that NFPA 70E has. Do any of you use the smaller calculated boundaries or do you use the 4 foot distance as the minimum??
b.t.w. Nice Forum!
PostPosted: Wed Jul 04, 2007 3:27 pm
4 Foot Boundary
We started out using the calculated numbers, but then decided it would be more consistant to adopt a standard "minimum" distance of 4 feet. We have a few distances greater than 4 feet but 4 is our minimum.
PostPosted: Wed Jul 04, 2007 3:33 pm
4 Foot Boundary
Joe B - what do you post on the labels? 4 ft?
PostPosted: Wed Jul 04, 2007 4:44 pm
4 Foot Boundary
We use the labels generated by the program so the distance will vary. We use 4 ft. as part of our electrical safety standard.
PostPosted: Tue Nov 20, 2007 10:50 am
Default Arc-Flash Boundary
The default arc-flash boundary for systems 600V and less is 4 feet. However, it depends on the available fault current and clearing time of the overcurrent protective device. According to NFPA 70E, the combination cannot exceed 300,000 Amp-cycles. What this means - is that if the available fault current is 50,000 amps, then the clearing time cannot exceed 6 cycles (100 milliseconds).
Ken Cybart
Littelfuse, Inc.