It is currently Fri Oct 23, 2026 11:51 am
 Post subject: How can the arc fault current be greater than the bolted figure?
PostPosted: Fri Feb 01, 2008 6:46 am
I have calculated the arcing current for a 900 volt supply and came up with an unexpected result. The bolted fault current is 20kA and the current in the arc came back as 24.88kA. I checked this with the web arc analyser and came back with the same result. Is there an explanation? Surely arc current cannot be greater than the available short circuit current?
I am using the following parameters; 900volts, MCC panel, 32mm gap, 457mm working distance, grounded supply, 20kA bolted current.
Any ideas?
Mike :confused:
PostPosted: Mon Feb 04, 2008 6:47 am
Mike :confused:
Congratulations! You've found one of the few anomolies with the 1584 equations! For more information, you should read http://us.ferrazshawmut.com/arcflash/getting_help/downloads/ICPS-wilkins011904_web.pdf
Hopefully these will be ironed out with the upcoming (someday, soon, sometime, almost here :rolleyes: ) NFPA/IEEE effort.
