jghrist wrote:
How do you establish an electrically safe work condition when the incident arc energy exceeds 40 cal/cm²? This sometimes occurs on the line side of 480 V main breakers fed by utility transformers that have no secondary protection.
You could have the utility deenergize the transformer primary. There may or may not be a visible open disconnect when this is done. As I read 70E Article 120, you need to use a voltage detector to test each phase to verify that it is deenergized before working on the main breaker. Voltage testing is listed in Table 130.7(C)(9) as a task, so this would indicate that it is considered "interacting" with the equipment and would require PPE. How can the voltage testing be done?
Reducing the Ei is the best way, or recalculate your Ei for the working distance the person will be at when doing the voltage testing.
jghrist wrote:
Is manually tripping the main breaker considered "interacting" with it, thus requiring PPE for the line side arc incident energy? If so, how is this done when the incident energy is >40 cal/cm²?
Yes, this is "interacting" with the equipment, remote switching is a popular solution for this.