| Post subject: | Table vs Incident Energy method |
Is the choice to use the table method vs the incident energy method up to the person doing the study? It does not seem to say in NFPA 70e that incident energy method should be used, but if such and such use the table method. It seems to be an either/or assuming you can meet the conditions in the table method. For example, I have a building that has never had a study done. The building is super critical, shutting down is "out of the question" and opening the equipment involved would not be safe while energized. The equipment seems to fit into the table method criteria, but I am getting a lot of pushback from more experienced Arc Flash Study folks about even considering the table method. Is there something I am missing as to why it is not desirable? |
| Author: | wbd [ Mon Jan 10, 2022 5:55 am ] |
| Post subject: | Re: Table vs Incident Energy method |
Seems if the building is super critical, there should be an up to date set of electrical drawings that may have a lot of information and if "super critical" seems like a study would have been done on the electrical system to determine such things as short circuit currents and protection/coordination. That being said, how do you know the parameters (fault current and clearing time) are being met to use the tables without a study? |
| Author: | aguywithfeet [ Mon Jan 10, 2022 6:07 am ] |
There is an up to date set of drawings but 1584 says field verification is necessary. Our policy has been to put eyes on everything we are putting in the study. The only things I can't get from the front of the panels is the wire size. I can see breaker types, most settings, etc. With breaker models I can get max clearing times. The loop feeding this building was studied this year by an engineering firm, so i have available fault current at the transformer. |
| Author: | aguywithfeet [ Mon Jan 10, 2022 6:13 am ] |
If you went by the prints alone. Would you assume the trip settings are at highest setting? |
| Author: | aguywithfeet [ Mon Jan 10, 2022 7:00 am ] |
Someone brought up that you would not actually know the fault clearing time of each sub breaker, especially if the fault is small. Also, you can't determine what the available fault current is downstream without a lot of work. So i guess using the prints and listing assumptions is the best method? |
| Author: | wilhendrix [ Mon Jan 10, 2022 4:14 pm ] |
In my view, the table method is meant to satisfy folks with smaller electrical systems. If your building is as critical as you say, you should get a full study done as well as a coordination study. Most of the time, the really high hazards are at the main or mains. Past the mains, the hazards usually fall off a lot. Remember, I’m not considering step down transformers of any size. 480 to 120/208 volt transformers can produce high arc flash hazards. When you say your building is super critical, several questions come to mind. For example, is there a second switchgear and feeder to the facility? Critical facilities like WWTP or hospitals almost always have two utility feeders, two services and a tie breaker to connect the two services together. If not, then your owner is not treating the building as critical or does not know there is stuff they should do to help insure the power is kept on. It's been my experience that people will often say it's critical, but won't spend the money to have real switchgear, two utilities and pay for the maintenance to keep such a critical plant properly running. Do you have multiple generators and UPS to back up the critical processes? If not, it’s not nearly as critical as the owner would have you believe. If you do get a full arc flash study, you’ll likely find a few “land mines” waiting to explode. By land mines I mean things could take your site down for hours or longer. |
| Author: | JBD [ Tue Jan 11, 2022 1:05 pm ] |
aguywithfeet wrote: There is an up to date set of drawings but 1584 says field verification is necessary. Our policy has been to put eyes on everything we are putting in the study. The only things I can't get from the front of the panels is the wire size. I can see breaker types, most settings, etc. With breaker models I can get max clearing times. Was the wiring verified to comply with the drawings during installation? Maybe signed check-off lists are available. Have you considered doing the study using multiple conditions such as, with the expected wire size, with one size smaller than expected, and one size larger? |
| Author: | aguywithfeet [ Mon Jan 24, 2022 8:59 am ] |
@ JBD: I do not like saying anything is for sure here unless i physically put eyes on it. We usually do a 120% of utility fault and a 50% of utility fault to try and account for any errors. To the other replies: I can assure you to everyone involved including my bosses, i will not be allowed to shut anything down and likely not able to open anything other than the large main switchgear. We had an "incident" the day after i posted this. The more i read about the table method though, it will be almost impossible to use unless i basically perform an analysis using SKM first anyways. Correct? |
| Author: | Jim Phillips (brainfiller) [ Mon Jan 24, 2022 9:45 am ] |
The "Table Method" is a carry over from the original HRC tables introduced in the 2000 Edition of NFPA 70E. It was in response to the arc flash hazard that was recognized in the previous edition of NFPA 70E - 1995. Over subsequent revision cycles the notes were added to address "reality" that the hazard also depends on short circuit current and arc duration. During the latest 70E first revision cycle meeting last summer, the tables were once again a topic of discussion (and some debate) They continue to remain as is which as you point out, requires short circuit current, clearing time etc. If it is desired to provide more detail, then IEEE 1584 is the way to go. The NEC tried to "help" by requiring the fault current and clearing time be on a label for service equipment rated 1200 Amps and greater in 110.16(B). |
| Author: | mayanees [ Mon Mar 14, 2022 10:05 am ] |
aguywithfeet wrote: @ JBD: I do not like saying anything is for sure here unless i physically put eyes on it. We usually do a 120% of utility fault and a 50% of utility fault to try and account for any errors. To the other replies: I can assure you to everyone involved including my bosses, i will not be allowed to shut anything down and likely not able to open anything other than the large main switchgear. We had an "incident" the day after i posted this. The more i read about the table method though, it will be almost impossible to use unless i basically perform an analysis using SKM first anyways. Correct? You're correct in saying you should just do an SKM analysis, surely if the package is available to you and if you know the contribution on the primary of the system. As long as you can determine an accurate value for the incident energy levels, it's appropriate to disassemble the equipment while energized to get any necessary trip unit information. I usually consider the cable ampacity to equal the rating of the breaker, so I don't disassemble panels for cable sizes. It must have passed an electrical inspection when initially energized. I'll spell that out in a proposal to the client, and will verify cable sizes if that's what they want, but I don't recommend it as money well spent. And if you have an up-to-date maintenance contract with SKM - use them! They're still good with their tech support, in my opinion. Good luck. |