| Author: | Homerjs78 [ Wed Jun 25, 2008 7:33 am ] |
| Post subject: | "Need not be considered" |
I see most interpret this statement the same but there seem to be several schools of thought when it comes to posting the hazard category. The two I am interested in are: 1. Label equipment as PPE #0 2. Label equipment whatever the min required PPE is for the plant (sometimes PPE #2) What are people doing for equipment that falls in this group? I am referring to the fourth paragraph on page 6 of the 2002 IEEE 1584. any comments are welcome. |
|
| Author: | Zog [ Wed Jun 25, 2008 9:18 am ] |
| Post subject: | |
Just because IEE thinks an arc below this level will not be self sustaining dosent mean there isnt a hazard. How to label this equipment should be discussed with you and your client. I usually recommend using the tables for this equipment. |
|