It is currently Mon Nov 09, 2026 6:56 am
 Post subject: MV Switchgear Fuse Holder. HCB, VCBB, or VCB?
PostPosted: Wed Mar 11, 2020 9:01 am
Hi all,
I have trouble choosing electrode configuration for a medium voltage switchgear with a fuse holder inside one of the cabinet.
i know that IEEE didn't really say what's the electrode configuration for a fuse holder is. It can be HCB where the clip is, or it can be VCB where the cable connect to the fuse. So i'm wondering what configuration you guys normally use for a fuse holder?
Thanks.
Khanh
 Post subject: Re: MV Switchgear Fuse Holder. HCB, VCBB, or VCB?
PostPosted: Mon Mar 16, 2020 8:42 am
Normally, HCB produces a larger value of arc flash energy. But you may want to be safe and try both and then take the greater value of Arc Flash energy and put that information on the AF label.
PostPosted: Mon Mar 23, 2020 10:23 am
If I may expand on Mr. Fuhr's excellent suggestion.
1) look at the direction of the current conductors feeding the arc... the force vector pushing the arc is created by those conductors. If there are clips and or lugs it may be better represented as HCB even if the cables come vertically.
2) Generally HCB vs VCB produces very similar arcing current, so HCB is the most conservative with respect to incident energy and usually arcing current as well.
3) However, if you are setting the protection tightly make sure you identify the lowest possible arcing current and ensure the protection will respond as you wish it to respond to that lower arcing current with margin for safety.
4) Regardless what model you use you want to make sure you have the right "time" in the equation!
5) If in doubt about the gap, use the largest gap that may be the case... larger gap is always more conservative.
File comment: Some charts showing incident energy at HCB, VCB VCBB, for 4.16 & 12.47 kV. 36 inches, 100ms, Std box at V. NOT INTENDED TO replace a proper Ei calculation, but may help to understand the impact of the decision you are pondering. Ei is roughly proportional to time.
5k 15kv AF charts.docx [122.96 KiB]
Downloaded 626 times
PostPosted: Fri Mar 27, 2020 1:18 pm
Thanks all for replying. ETAP let me put in two electrode configurations and it would show the worse one. I put in HCB and VCBB.