What bus gap do you use for the low voltage secondary of transformers?
Actual gap 12%  12%  [ 3 ]
IEEE 1584 values of 25 or 32 mm 80%  80%  [ 20 ]
Something else 0%  0%  [ 0 ]
We don’t perform/require studies 8%  8%  [ 2 ]
Total votes : 25
Author Message
 Post subject: Transformer Secondary Bus Gap for Calculations?
PostPosted: Sun Oct 04, 2020 2:41 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
We had an interesting question last week regarding incident energy calculations and the gap distance on the low voltage secondary of transformers. The bus gap is often quite large - normally 6 inches or greater. So, the question that a forum member asked is if people use the actual large gap (I would question arc sustainability) or do you use one of the standard IEEE 1584 values like 25 or 32 mm? I promised I would ask the group as part of this week's Question of the Week.

BTW, if you have a question you would like to see asked, let me know!

So here is the question:

What bus gap do you use for the low voltage secondary of transformers?

Actual gap
IEEE 1584 values of 25 or 32 mm
Something else
We don’t perform/require studies


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883