It is currently Tue Nov 10, 2026 8:51 pm
Do you wear arc rated PPE when Table 130.5(C) states NO likelihood of occurrence of an arc flash?
Yes 55%  55%  [ 39 ]
No 15%  15%  [ 11 ]
Sometimes – It depends (please comment) 30%  30%  [ 21 ]
Total votes : 71
 Post subject: Arc Rated PPE - Likelihood of Occurrence of Arc Flash = No
PostPosted: Sun Jan 24, 2021 3:46 pm
This week’s question is a variation on one that I asked a couple of weeks ago.
NFPA 70E Table 130.5(C) Estimate of the Likelihood of Occurrence of an Arc Flash Incident lists operation of a circuit breaker, switch, contactor, or starter as “NO� for likelihood of occurrence of an arc flash for “Normal Equipment Condition.�
Normal condition is defined by 110.4(D) and includes the equipment being properly installed, properly maintained, used in accordance with instructions, doors are closed and secured, covers in place, no evidence of impending failure.
With that intro, here is this week’s question:
Do you wear arc rated PPE when Table 130.5(C) states NO for likelihood of occurrence of an arc flash?
Yes
No
 Post subject: Re: Arc Rated PPE - Likelihood of Occurrence of Arc Flash =
PostPosted: Mon Jan 25, 2021 8:43 am
Our company policy is that if we are working around energized equipment, then we always wear AR clothing, even if the AF level is less than 1.2 Cal/cm2.
PostPosted: Mon Jan 25, 2021 9:29 am
That's the comment I was hoping to hear! Thanks Bob!
PostPosted: Sat Jan 30, 2021 6:59 am
Our company policy is when interacting with energized equipment, proper PPE for arc flash hazards must be worn. Might be more than needed but trying to teach everybody how to ensure electrical equipment meets the requirements for not needing PPE seemed very onerous. Teach that even wearing arc rated PPE per the label can result in injury.
PostPosted: Wed Mar 24, 2021 1:06 pm
Jim
do you want to comment on the 2021 70E removing the <= 1.2 cal table.
PostPosted: Sun Mar 28, 2021 3:05 pm
Flash wrote:
Jim
I'm assuming you meant PPE Category 0 which was < 1.2 cal/cm2?
The requirements for Category 0 were already inherent in NFPA 70E i.e. eye protection, natural fiber etc. so it was removed in 2015. - let me know if I misunderstood the question.
