Which short circuit calculation method do you use?
ANSI/IEEE 72%  72%  [ 23 ]
IEC 13%  13%  [ 4 ]
Both 9%  9%  [ 3 ]
Other (please describe) 3%  3%  [ 1 ]
I Don't Perform Studies 3%  3%  [ 1 ]
Total votes : 32
 Post subject: Short Circuit Calculations: ANSI/IEEE or IEC
PostPosted: Sun Sep 15, 2019 12:47 am
I just arrived in Geneva, Switzerland for IEC meetings which prompted this week's question. It is about IEC vs. ANSI/IEEE Standards for short circuit current calculations.
Depending on which method is used, the results can vary a bit which may also affect the calculated incident energy.
Here is this week's question:
ANSI/IEEE
IEC
Both
 Post subject: Re: Short Circuit Calculations: ANSI/IEEE or IEC
PostPosted: Sun Sep 15, 2019 7:41 pm
ANSI/IEEE
IEC
Both
I prefer comprehensive method factoring in all the equipment active, reactive impedance and contribution to fault current. Also, I find it important to know the range of available fault current (min - max) and take into account arc duration so I can identify worst case arc flash scenario. Incident energy alone is meaningless unless you know how fast that energy has been delivered. Jim, let me know please if I can be of any help elaborating on or escalating this issue to decision making authorities.
Michael Furtak, C.E.T.
http://arcadvisor.com