It is currently Wed Nov 11, 2026 4:05 am
 Post subject: Open Delta Modeling
PostPosted: Fri Jul 18, 2014 11:49 am
I have a service fed by 2 - 100kVA transformers set up as an open delta. The primary side is connected as a grounded wye at 46kV and the secondary is a open delta with a center tap. The secondary voltages are then 120/240 and 208.
How would you model this for arc flash hazard?
 Post subject: Re: Open Delta Modeling
PostPosted: Thu Jul 24, 2014 9:23 am
For arc flash analysis, I would model it as a full delta with 240V phase to phase voltage.
