It is currently Mon Oct 05, 2026 11:36 am
 Post subject: Arc Flash Analysis
PostPosted: Wed Jun 04, 2014 10:15 am
What are the minimum IEEE1584 requirements used to determin which electrical equipment requires an Arc Flash Analysis?
 Post subject: Re: Arc Flash Analysis
PostPosted: Wed Jun 04, 2014 3:12 pm
IEEE 1584 doesn't really provide a list of what to include. NFPA 70E attempts to do this based on what equipment is required to have an arc flash label.
Section 130.5(C) Equipment Labeling. Electrical equipment such as switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control centers .. It is not an all inclusive list since there are many other types of equipment. The section also tries to add clarification with the text: “... and are likely to require examination, adjustment, servicing or maintenance while energized�
The reason the label article is important is this often drives the scope of the study. i.e. include what get's labeled. Also, if IEEE 1584 calculation methods are used (which is what the various software is built upon) the equations are valid for three phase systems and not for single phase so that limits how far you may go as well.
I asked a series of "Question of the Week" questions a while back and asked our group at the forum about other types of equipment not listed in NFPA 70E. You can check out this section near the top of the forum.
All of this was rolled into a short article that was published in the January 2014 Edition of Electrical Contractor Magazine which may be of help.
Others may have additional guidance.