It is currently Wed Sep 30, 2026 10:27 am
 Post subject: Arc Flash for SWBD c/w Main BKR & Feder BKR's
PostPosted: Wed Jan 14, 2009 8:22 am
In regards to calculating energy and attaching arc flash labels to switchboards / panels (which has main breaker and many feeder breakers), I appreciate if anyone who's familiar with NFPA, IEEE and safety practices to clarify the following:
1-Where do we consider calculating the energy on the switchboard / panel (on the line side of the main breaker, or the load side of the main breaker)?
2-Do we require attaching labels on each breaker of the switchboard / panel ? If that’s requested by the client, in this case, do we consider calculating the energy after the breaker (on the load side) or before the breaker (on the line side) of each breaker ( Main or Feeder)?
I appreciate your opinions, Thank you !
PostPosted: Wed Jan 14, 2009 10:07 am
It sounds to me from your post that your company has been hired to do this analysis, I would hope that you are familar with NFPA 70E and IEEE.
Both
You calulate the Ei for the equipment, if you are talking about a breaker then you need to consider what is feeding it for your analysis.