 Post subject: NFPA 70E. 130.5(G) Note
PostPosted: Fri Sep 08, 2023 9:56 am
Does anyone know the purpose for the note on 130.5(G) in NFPA 70E, where it prohibits the use of table 130.7(C)(15)(c) in specifying PPE categories. As an example, if the IE analysis shows we have 30 cal/cm^2, why is it prohibited to look at this table and know that we need to specify category 4 clothing?
 Post subject: Re: NFPA 70E. 130.5(G) Note
PostPosted: Tue Apr 29, 2025 11:07 am
There is a loophole you can use.
Your company is allowed to create your PPE selection process that uses "Classification" groups similar to the PPE Categories in NFPA70E.