stevenal wrote:
A consultant proposed the threshold.
To clarify my question: Can we (not) invoke the exception on a case by case basis as illustrated above (regardless of where the threshold is drawn)? Or must we make one decision utility wide?
Seems your question is....could you use the exception in selected cases and do an analysis for others. Good question! Since the standard says "in lieu of" it would seem you would need to do either one or the other. As with 70E, the consensus is use the tables if appropriate or do the study, but no mixing of options. Will be interesting to hear from other folks as well.
We have taken the approach that due to the sheer number of devices, different levels of fault duty, and clearing times on a distribution system it is not practical or meaningful to attempt to calculate IE for each device and each possible connection scenario. We have taken "typical" systems and equipment at various locations and sizes to determine the level of PPE for below 1000 volts and use this system wide. Our basic approach is to always de-energize if possible.